Originally Posted by
theskilledworker
The house has a 60 amp service, I'll upgrade it to a hundred. I'll charge about $1200 - $1500 using aluminum feed conductors. That's from the top of the point where the overhead wires attach, through the meter base and into the panel. The new aluminum is a much stronger alloy from what we used to have in the '70's and is vastly cheaper. We used it even in very high end homes as panel feeds.
Changing a service from 60 amp to 100 amp would be a disservice to any of my customers. For a few more bucks you could go to 200 amp. This is the average upgrade. While I agree some homes are smaller and have low power demands, future installations must be considered. Just the addition of a heat pump for example, that 100 amp panel has to come back out and another service upgrade would be required.
(Canadian code generally runs pretty much as NEC so I'm making an assumption). #14 is used in commercial and industrial too if not specified by the engineer, although it used to be standard to use #12 (one size heavier gauge) everywhere but in homes.
Canadian codes are very different from the NEC.
Also, #12 minimum has never been a requirement in industrial, commercial or residential installations. I have worked in factories where it was SOP. But it was never a requirement by the NEC. I heard the same "old wives tale" when I was an apprentice.
I refuse to hide junctions, it's against code and my own standards of workmanship.
It's against the NEC. That itself covers anyones standard of workmanship.
By the way, home inspectors in our area can't take the cover off a panel let alone dig deeply enough to assess the real state of a home's wiring. If he sees "knob and tube" in the basement, he would be right to assume that the whole house needs rewiring and put in a number of say $4,000 to 10,000 depending on the size of the house.
Correct on the "Home Inspectors" But incorrect on the K&T. In most jurisdictions, if the house wiring (branch circuits) is not touched, extended or modified when performing a service upgrade, there would be no requirement to upgrade the K&T.
We have 125 amp services in our area, most go to 200; never heard of 150. Your service conductors are likely not rated for more than 100. You can have an electrician upgrade your panel to a 40 cct 100 amp panel, which might be enough, of you heat with natural gas or propane. And as I said, if existing wiring has not been damaged and has a ground wire in it, no reason to replace it. In our area, new code measures are generally for new construction and for major renovations, not necessarily retroactive to existing. For example, if a kitchen has split receptacles, a home purchaser shouldn't demand they be changed to T-slot 20 amp, etc. If wiring has been properly installed it should remain reliable, although new outlets can be installed for convenience.
150 amp panels are common and found in home depots and Lowes. If they do not have them, any electrical supply house will.
I have never seen a 100 amp 40 space panel? Only a 100 amp 30 space. Like said before. The branch circuit wiring in most every case will not need to be upgraded, even if it has no ground wire (EGC) included. Ungrounded branch circuits can be protected with the addition of GFCI's should the HO want them installed.
The use of 15 amp receptacles on 20 amp circuits in kitchens and other household branch circuits are compliant, anywhere in the home, new construction or not.